请问;消防水泵是不是应设过载保护啊?
请教了。。。 <p class=MsoNormal style="MARGIN: 0cm 0cm 0pt"><font size=3><span style="FONT-FAMILY: 宋体; mso-ascii-font-family: 'Times New Roman'; mso-hansi-font-family: 'Times New Roman'">消防水泵是灭火救援的重要设备,在消防灭火中起着极为重要的作用。按照我们的习惯性思维,凡是重要设备就应设过载保护。但《民规》第</span><font face="Times New Roman"><?xml:namespace prefix = st1 ns = "urn:schemas-microsoft-com:office:smarttags" /><st1:chsdate w:st="on" IsROCDate="False" IsLunarDate="False" Day="30" Month="12" Year="1899"><span lang=EN-US>8.6.3</span></st1:chsdate><span lang=EN-US>.5</span></font><span style="FONT-FAMILY: 宋体; mso-ascii-font-family: 'Times New Roman'; mso-hansi-font-family: 'Times New Roman'">条、第</span><span lang=EN-US><font face="Times New Roman">10.2.2.4</font></span><span style="FONT-FAMILY: 宋体; mso-ascii-font-family: 'Times New Roman'; mso-hansi-font-family: 'Times New Roman'">条(</span><span lang=EN-US><font face="Times New Roman">3</font></span><span style="FONT-FAMILY: 宋体; mso-ascii-font-family: 'Times New Roman'; mso-hansi-font-family: 'Times New Roman'">)条规定:“对于突然停电会导致比因过负荷而造成损失更大的配电线路,不应装设切断电路的过负荷保护电器(如消防水泵的供电线路),但应装设过负荷报警电器”。照此规定,<strong>消防水泵不应装设过载保护切断装置</strong>。这主要是考虑到火灾发生时,应全力保证消防用水的需要,因为由于水泵过载可能造成的线路、设备损失与火灾损失相比微不足道。</span></font></p> 消防水泵是应设过载保护,但不设漏电保护,在电器控制柜内空气开关等同<font size=3><strong>过载保护切断装置,热继电器也是过载保护装置,在火灾报警主机上是严禁用</strong></font><font size=2>漏电保护器的,并且要直接接在开关上,不允许用插座的</font> 同意<strong><font size=2>二楼观点</font></strong> 不太清楚到底是要还是不要,我觉得既要热保护,又要双备份更好,这是个尽量降低出事故的几率问题。 个人觉得如果水泵要加过载保护的同时也就是承认整个的设计就有问题了 谢谢分享 :)好像不用设吧 消防水泵---------要是不设过载保护,故障信号从什么地方获得?水泵又如何完成自动切换的? 2楼说得有道理哦。3楼也有道理。9楼也有道理。我疑惑了。
不过实际工作中,控制箱都有空开和热继的,这也算是过载保护了。
所以,实际都是接了的。
页:
[1]
2